Dear equest users,

Today morning after doing the LPD calculation in excel i discovered
something that is LPD calculation in eQUEST 3.65 which can be new for few
or many people.

This can be implemented when one know the Lighting power of the fixture and
number of fixtures.

There is a very innocent way to do it that is we can multiply the number of
fixtures and lighting power in calculator and then input the lighting load
in kW in the internal load where there is space for lighting power.

Then we can come up with the lighting power density in the corner space of
the same window.

After this one can remove the lighting loads in kW and put in watts per
square feet that is the lighting power density.

I will have the snapshot of the same dialogue.

[image: Inline image 1]

[image: Inline image 2]

We can come up with the above snapshot that the 0.012 kW results in 0.044
watts per square feet of LPD which can be treated as LPD calculation by me.
The actual area in the model calculates it.

Thanks,

Sharad.Kumar|Engineer.

Green Horizon Consulting LLP.

Gurgaon.

India.

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Hi Sharad,
Alternatively, once you enter the lighting power KW, you can just use the user expression : LOCAL("LIGHTING-KW")*1000/LOCAL("AREA"), the LPD will get updated by itself.

Regards,Rathnashree

Dear equest users,
Today morning after doing the LPD calculation in excel i discovered something that is LPD calculation in eQUEST 3.65 which can be new for few or many people.
This can be implemented when one know the Lighting power of the fixture and number of fixtures.
There is a very innocent way to do it that is we can multiply the number of fixtures and lighting power in calculator and then input the lighting load in kW in the internal load where there is space for lighting power.
Then we can come up with the lighting power density in the corner space of the same window.
After this one can remove the lighting loads in kW and put in watts per square feet that is the lighting power density.
I will have the snapshot of the same dialogue.

We can come up with the above snapshot that the 0.012 kW results in 0.044 watts per square feet of LPD which can be treated as LPD calculation by me. The actual area in the model calculates it.

Thanks,Sharad.Kumar|Engineer.Green Horizon Consulting LLP.Gurgaon.India.

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send? a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

I?d also insert:

1. There is no functional or accuracy advantage to entering lighting loads as an LPD once you know and have entered the loads as kW. In fact, there is the possibility you?ll accidentally leave both inputs entered, which will end up doubling the lighting loads (these inputs are additive).

2. If your purpose is to determine the lighting power density for the entire building, here?s the method I presently use as a balance of efficiency/accuracy:

a. File ? Export File ?Space Loads Report (CSV) [and Open it when the dialog comes up]

b. Note the Activity Description column, if your project was generated via the Wizards, you should probably observe a consistent marker for your plenum spaces: ?(unknown)?

c. Use some if/then logic in excel to sum lighting power installed outside plenums, and then divide by the associated sum area. (note space area is a separate column available).

Best of luck!

~Nick

Nick Caton, P.E.

Senior Energy Engineer
Energy and Sustainability Services
North America Operations
Schneider Electric

D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com
F 913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Thank you all.I never realized it would be double counted.
Regards,Rathnashree

I?d also insert: ?1.?????? There is no functional or accuracy advantage to entering lighting loads as an LPD once you know and have entered the loads as kW.? In fact, there is the possibility you?ll accidentally leave both inputs entered, which will end up doubling the lighting loads (these inputs are additive).? 2.?????? If your purpose is to determine the lighting power density for the entire building, here?s the method I presently use as a balance of efficiency/accuracy:a.?????? File ? Export File ?Space Loads Report (CSV)? [and Open it when the dialog comes up]b.????? Note the Activity Description column, if your project was generated via the Wizards, you should probably observe a consistent marker for your plenum spaces: ?(unknown)?c.?????? Use some if/then logic in excel to sum lighting power installed outside plenums, and then divide by the associated sum area.? (note space area is a separate column available). ?Best of luck! ?~Nick ?Nick Caton, P.E.
| ? Senior Energy Engineer
? Energy and Sustainability Services
? North America Operations
? Schneider Electric | D??913.564.6361
M??785.410.3317
E??nicholas.caton at schneider-electric.com
F??913.564.6380 | 15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States |
| |

? ?

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Hi Rathna,

Could you please tell me the findings from the following equations.
The thing without doing it in eQUEST 3.65 is that
LOCAL("LIGHTING-KW")*1000/LOCAL("AREA")
may result in some other things as i know.

Actually i am unable to get the findings.
The things that i am able to interpret is that you will have the LPD (
watts per square feet) from this as per you.

Could you please tell me how without inputting kW one can get the
results anyhow. This seems to me to be me miscalculation and
mis-interpretation as per me as if you will input kW as power then there is
left no means to calculate the LPD as watts per square feet as this is not
within the limitations of eQUEST anyhow.

Thanks,

Sharad.Kumar|Engineer.

Green Horizon Consulting LLP.

Gurgaon.

India

.......................................................................................
..........................................................
........................................................................

Hi Sharad,

Alternatively, once you enter the lighting power KW, you can just use the
user expression : LOCAL("LIGHTING-KW")*1000/LOCAL("AREA"), the LPD will get
updated by itself.

Regards,

Rathnashree

.............................................................................................................

............................................................
.................................................

You can also use a BDL expression to do the same thing automatically and
eliminate a step. For example:

10*(#L("AREA"))

Where ?10? is the wattage of the installed lights in the space and
?#L(?AREA?)? grabs the area of the space in which the lighting load is
being applied.

I hope this helps.

Sincerely,

incerely,

[image: ARCH | NEXUS]
DAVID W. GRIFFIN II
BEMP
ENERGY ANALYST
2505 E Parleys Way
Salt Lake City, UT 84109
*Office* 801.924.5028
archnexus.com
[image: Twitter] [image: Facebook]
[image:
Youtube]
[image:
LinkedIn]

[Note about the above e-mail]:

Thanks Griffin, but the above message can help only when the lighting load
is 10 watts for one fixture but my post has been in general like any
lighting power calculations can be done by my way.

Your way is to help with one lighting load but as per my e-mail the
lighting fixtures and their number can help to do the calculations.

Also one thing is missing that the window dialogue (as shown in
my snap-shots) has both lighting load as watts per square feet and kW which
can be input as one at one time.

Thanks,

Sharad.Kumar|Engineer.

Green Horizon Consulting LLP.

Gurgaon.

India

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

I am not understanding the question. You can input the lighting power as kW or as W/ft2 ? the results will be the same. You can input both kW and W/ft2 and the total lighting power will be the sum of the two. Note, in the LV-B report, the lighting power is always reported as LPD (W/ft2) regardless of how you do the input. The Lighting dialog reports the total lighting power as you input:

[cid:image004.png at 01D1D1DC.10604550]

[cid:image005.png at 01D1D1DC.10604550]

[cid:image006.png at 01D1D1DC.10604550]

[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056

www.wspgroup.com

Anonymous's picture
Anonymous