Dear all
When using appendix G of ASHRAE 90.1-2007 to build baseline, If the baseline system is system 3 (PSZ-AC) , 4 (PSZ-HP) or 5 (Packaged VAV with reheat) ,which table in ASHRAE90.1-2007 should be used to decide the Equipment efficiency separately? Table 6.8.1A or 6.8.1D?
Thank you for your help
Aarron
6.8.1A is appropriate for packaged systems.
The other table (6.8.1D) applies to single-room air conditioners.
Best to you,
Dave
I have a similar question, If my system is 2 (PTHP) can I use table
6.8.1B or 6.8.1D and why?
thanks
Oscar.