I will give much praise to the person who can figure out why I have such an imbalance in the heating and cooling loads for the attached ASHRAE 90.1 2010 baseline model. I've been troubleshooting the model for a few days now. I'm sure it's something completely obvious, and I'll be quite embarrassed by the solution.

Anyone up for the challenge?

[ARCH | NEXUS]
DAVID W. GRIFFIN II
BEMP
ENERGY ANALYST
2505 E Parleys Way
Salt Lake City, UT 84109
Office 801.924.5028
archnexus.com
[Twitter][Facebook][Youtube][LinkedIn]

via Equest-users's picture
Joined: 2016-07-15
Reputation: 200

Hi David,
How are the results different from what you are expecting? I don't see anything too unusual but I am not as familiar with SLC loads as you are.
One comment I have is that you have all constant-volume PSZ systems, one of which has 16 zones assigned to it. Without VAV and/or zonal reheat, you are getting many unmet hours in your zones. I would focus there.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image009.jpg at 01D2B901.3DC08A20] [cid:image010.jpg at 01D2B901.3DC08A20]

134 South Fitzhugh Street Rochester, NY 14608

T: (585) 698-1956 F: (585) 325-6005

bbishop at pathfinder-ea.com www.pathfinder-ea.com

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.

via Equest-users's picture
Joined: 2016-07-15
Reputation: 200

There is a huge disparity between heating and cooling loads (3-4% Cooling/42% Heating).