Heating Source Question

2 posts / 0 new
Last post

I am modeling an all-electric building. My baseline building is a system 8 PFP VAV with chillers and electric resistance heat.

We are considering adding natural gas water heaters for high dishwasher and shower loads. It does not seem like this should change the building to an electric/hybrid with the baseline system changing to system 7 with a hot-water gas boiler as the architect has suggested. The proposed HVAC heating source is still 100% electric.

Has anyone dealt with this heating source question? What was the resolution?

Thanks in advance,
Rick

R I C H A R D E L L I S O N
BEAP, BEP, BEMP, BESA, CBEP, CDSM, CEA,
CEM, CMVP, CTAB, DGCP, HBDP, LEED AP, PE
Manager of Energy and Simulation
Southland Industries
22340 Dresden Street, Suite 177
Dulles, VA 20166
Office: 703.834.5570
Direct: 703.834.2438
Fax: 703.834.5572

R I C H A R D E L L I S O N BEAP, BEP, BEMP, BESA, CBEP, CDSM, CEA, CEM, CMVP, CTAB, DGCP, HBDP, LEED AP, PE Manager of Energy and Simulation Southland Industries 22340 Dresden Street, Suite 177 Dulles, VA 20166 Office: 703.834.5570 Direct: 703.
Richard-Ellison's picture
Offline
Joined: 2011-09-30
Reputation: 1

Hi Richard,

My take is that the system type selections are based on the HVAC heating
energy source and are not dependent on the water heating source. If the
proposed HVAC system is all electric then System 8 seems to be the correct
choice.

For the water heating, the fuel source must be the same for baseline and
proposed.

However, if the building now has a gas supply, the design team may want to
evaluate the feasibility of a gas (HVAC) heating system.