[Hap-users] Wall Assembly - Steel Stud Framing

2 posts / 0 new
Last post

The Wall Properties Input Screen calculates the overall R and U values for a
sandwich assembly however it doesn't have any way to factor in the "framing
effect" of wall studs which can have a significant effect on average wall
assembly R and U values.

When I queried Carrier, part of Craig's reply was for cooling design loads
and energy modeling, ".U-value is not important, what is important is making
sure the specific heat, density and weight of the composite insulation/stud
layer is correct. Those values are used in the TFM equations not U-value."

Since this isn't as simple as inputting an overall U-Value from ASHRAE, Has
anyone come up with a way to effectively model steel stud framing that would
pass a DOE review?

Thank you,

Michael L. Hardy, PE, F.NSPE
Black Oak Engineering, Inc.
Cell 503.314.5244

MLHardy's picture
Offline
Joined: 2010-12-08
Reputation: 0

Wow, that's kind of alarming to hear. I always assumed the U-value was
more important. I approximate the framing effect by first inputting the
ASHRAE 90.1 assembly for a given wall/roof type, then reduce the R-value
of the insulation (not the other values) until the U-value matches the
value listed in Table A3.3 for the given amount of continuous
insulation. Then I would add in the additional layers of construction
(like brick veneer, block, etc..) that are in the actual design but not
part of the basic ASHRAE tabulated assemblies.