Fresh air calculation

2 posts / 0 new
Last post

I have provide a load calculation for a building which is supposed to have a chiller plant to provide cooling through a fan coil unit and an AHU system to provide just fresh air(outdoor air ventilation) through diffusers. some amount of chilled water will be supplied to the AHU to have the outdoor air treated. I have been using carrier HAP and my challenge is how to go about the system properties i.e equipment type and air system type.

thanks,

Mohamed Gasser's picture
Offline
Joined: 2016-05-18
Reputation: 0

?Hello,

For the system, under the General tab choose ?terminal units, 2-pipe fan coil (if they are cooling only) then choose common ventilation system. In the System components tab, you can describe the AHU - Central cooling, supply and return fans, etc. ?Then input the fan-coil unit description under the Zone components tab.

Aaron

Aaron Smith, P.Eng
M&R Engineering Ltd.

Sent from my BlackBerry 10 smartphone on the TELUS network.
? Original Message ?

Date: Sat, 22 Feb 2014 12:16:38 +0300
From: Mohamed Gasser
To: "hap-users at lists.onebuilding.org"

Subject: [Hap-users] fresh air calculation
Message-ID:
Content-Type: text/plain; charset="windows-1256"

I have provide a load calculation for a building which is supposed to have a chiller plant to provide cooling through a fan coil unit and an AHU system to provide just fresh air(outdoor air ventilation) through diffusers. some amount of chilled water will be supplied to the AHU to have the outdoor air treated. I have been using carrier HAP and my challenge is how to go about the system properties i.e equipment type and air system type.

thanks,