In the DOE-2 glass library I am looking at the double low-e (e3=.4) clear product, glass type code 2600.
Does anyone know what the e3=.4 means?? There are other products, such as type 2630 with e2=.1 with a much different assembly u-value.
Thank you,?Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513
An HTML attachment was scrubbed...
URL:
Sounds like we could benefit from an updated DOE-2 window library based on Bruce?s observations.
As to the meaning of ?e3=.4?, per Table 7 in the DOE-2 help entry for ?WINDOW Library?:
Low-E:
A low emissivity metallic coating is applied in order to increase thermal IR reflectance. The coated surface is indicated by en = v, where n = 1 is the outside of the outer pane, n = 2 is the inside of the outer pane, etc., and v is the emissivity (see, for example, G-T-C = 2635, where e2 = 0.1 indicates a coating with an emissivity of 0.1 on surface #2).
So, ?e3=.4? describes an assembly with a low-e coating of emissivity 0.4 on the inside surface of the inner pane.
Syracuse Glass has a good list of considerations for low-e coatings and whether to have them on the #2 or #3 surface. Generally, coat the #3 surface if heat loss is the primary consideration, and the #2 surface to limit solar heat gains.
http://www.syracuseglass.com/E-DOCS/Insulating%20Glass/EDOCS/LOW-E%20Coating%20Orientation.pdf
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image002.jpg at 01D32896.FC4F3090] [cid:image004.jpg at 01D32896.FC4F3090]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com www.pathfinder-ea.com
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
Thanks Bruce & Bill.?Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513
An HTML attachment was scrubbed...
URL: