Good morning,
For my model, when I go to report LS-C, Is not showing any roof conduction, not really sure why since I have a pitch roof as unconditioned attic/plenum, therefore there should be heat transfer from the outside to the attic and from the attic to the interior space.
How should I correct this?
Thanks.
Catalina Caballero, AIA. Assoc., LEED GA.
The SPACE definition should defined ZONE-TYPE = PLENUM, not
UNCONDITIONED. The ZONE definition should be TYPE = PLENUM, again
not UNCONDITIONED.
Note PLENUMs can also be defined with the SPACE definition as
ZONE-TYPE = CONDITIONED in the case of an atrium being used as a
return air plenum with lights, occupants, etc.
Catalina,
I am not sure about the Wizard mode, I haven't used it that much. I
tend to use the Detailed edit mode or direct edit in the .inp file.