Hi
Just a simple question. I want to type in the fan energy as kW/cfm. But it seems I cannot "activate" that input option. How do I switch from the SUPPLY-STATIC and SUPPLY-EFF to the SUPPLY-DELTA-T and SUPPLY-KW/FLOW option?
[cid:image001.png at 01CB8578.1B843510]
Best regards,
Per Topp
Hi Topp,
Just do right click on Static in WG tab and do default, then KW/CFM tab will
automatically activate.
Thanks,
Ashu
Right click on Static in WG (1.17 in your case) and select Restore Default. Design kW/cfm and Delta T will become available for input.
Best,
Ana
From: TOPP at orbicon.dk
To: equest-users at lists.onebuilding.org
Date: Tue, 16 Nov 2010 10:22:39 +0100
Subject: [Equest-users] Fan energy typed in as kW/cfm
Hi
Just a simple question. I want to type in the fan energy as kW/cfm. But it seems I cannot ?activate? that input option. How do I switch from the SUPPLY-STATIC and SUPPLY-EFF to the SUPPLY-DELTA-T and SUPPLY-KW/FLOW option?
Best regards,
Per Topp
Place your cursor over the ?Static in WG? box and right click and select
?restore Defaults? and the kW/cfm box becomes active.
Jeffrey G Ross-Bain, PE, LEED, BEMP