Error-HVAC System Zones have no Master Zones

2 posts / 0 new
Last post

Hello Everyone! I have modeled different zones to be "*Unconditioned*"
in "*Zone
Names and Characteristics*" Tab at Screen 2 of DD Wizard. Similarly, I have
unchecked the "*Conditioned*" button in "*Zone Group Definitions*" Screen
for each of these zones. But when I simulate the building I get the error
that the systems for these zones do not have master zones (Attached image).
Can someone help me out in solving this?

Thanks.

Dilshad Khan
(A Student)

Dilshad Ahmed Khan's picture
Joined: 2018-03-05
Reputation: 0

If i read correctly, unconditioned zones MUST be added to a conditioned zone and system. Unconditioned zones cannot by themselves.
It has been this way since the beginning of DOE-2 in 1981.
John R. Aulbach, PE
On Tuesday, May 14, 2019, 1:52:55 AM PDT, Dilshad Ahmed Khan via Equest-users wrote:

Hello Everyone! I have modeled different zones to be "Unconditioned" in "Zone Names and Characteristics" Tab?at Screen 2 of DD Wizard. Similarly, I have unchecked the "Conditioned" button in "Zone Group Definitions" Screen for each of these zones. But when I simulate the building I get the error that the systems for these zones do not have master zones (Attached image). Can someone help me out in solving this?