eQ_WthProc for weather file conversion error: invalid floating point

5 posts / 0 new
Last post

Dear Equest comunity,
I?m a beginner using eQ_WthProc convertor. When I try to convert a EPW weather file into a BIN file, it appears an error message "11.7 invalid floating point", and that number "11.7" is the first value to read. I don?t know what is the problem, I hope you can help me out with this problem.
Emmanuel Hernandez

emmanuel hernandez martinez's picture
Joined: 2013-01-07
Reputation: 0

Emmanual,

I have found the routine outlined by Susan Trzos to be helpful.
You must copy files into locations exactly as noted, or it will not work.

*
*

*Arpan Bakshi** *LEED AP BD+C, ESTIDAMA PQP

NYCCTgreen's picture
Offline
Joined: 2011-09-30
Reputation: 0

The link to The post is: http://energy-models.com/forum/equest-pumps-aux#comment-4660

Joe's picture
Joe
Offline
eQUEST User
Joined: 1969-12-31
Reputation: 2200

I have the same problem: '-7.3' is not a valid floating point value'. I followed the routine step by step and also go throught the forum and tried all options but the error is still the same...Can anyone give me some advice?Thanks!

Valeria Fiorentino
Valeria Fiorentino's picture
Joined: 2013-09-23
Reputation: 200

A possible answer:

I was having the same problem.

My computer has windows in Spanish as OS, with regional options with "," for decimal separation.

I changed this regional settings in Windows and the processor worked perfectly afterwards.

Best

DarĂ­o

www.riosustentavel.com.br