Water Source Heat Pumps as Dedicated Outside Air Units

4 posts / 0 new
Last post

Hello All!

I am having an issue regarding a dedicated outside air unit that takes advantage of a condensing water loop.

When modeled as a water source heat pump (TYPE = HP), eQUEST gives me an error saying this system type is not eligible for "OA-FROM-SYSTEM".

One of my thoughts is to

* model all the units served by the outside air unit with no fresh air

* model the dummy zone with a summation of the fresh air required by the spaces served

But then that might interfere with a proper simulation of mixed air temps going into the space.

Thoughts?

***ERROR***********************************************************************

OSAU is not a legal SYSTEM-TYPE to be

an OA-FROM-SYSTEM. SZRH/PSZ/RHFS/MZS/PMZS/DDS/VAVS/PVAVS/PVVT

RHFS/IU/PIU/PTGSD/EVAP-COOL/RESYS2 are allowed.

Jesse Eisenhart

Jesse Eisenhart's picture
Offline
Joined: 2011-12-21
Reputation: 0

I guess I stumped everyone. :)

Jesse Eisenhart

Jesse Eisenhart's picture
Offline
Joined: 2011-12-21
Reputation: 0

Can you use PVVT, but configured as you would have setup the heat pump?

David

*
*

*David S. Eldridge, Jr.**, P**.**E**.**, LEED AP BD+C, BEMP, BEAP, HBDP*

* *

*From:* equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jesse Eisenhart
*Sent:* Tuesday, April 03, 2012 3:21 PM
*To:* equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] Water Source Heat Pumps as Dedicated Outside
Air Units

I guess I stumped everyone. J

Jesse Eisenhart

*From:* equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jesse Eisenhart
*Sent:* Tuesday, April 03, 2012 11:07 AM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] Water Source Heat Pumps as Dedicated Outside Air
Units

Hello All!

I am having an issue regarding a dedicated outside air unit that takes
advantage of a condensing water loop.

When modeled as a water source heat pump (TYPE = HP), eQUEST gives me an
error saying this system type is not eligible for ?OA-FROM-SYSTEM?.

One of my thoughts is to

? model all the units served by the outside air unit with no fresh
air

? model the dummy zone with a summation of the fresh air required
by the spaces served

But then that might interfere with a proper simulation of mixed air temps
going into the space.

Thoughts?

***ERROR***********************************************************************

OSAU is not a legal SYSTEM-TYPE to
be

an OA-FROM-SYSTEM. SZRH/PSZ/RHFS/MZS/PMZS/DDS/VAVS/PVAVS/PVVT

RHFS/IU/PIU/PTGSD/EVAP-COOL/RESYS2 are allowed.

Jesse Eisenhart

David S Eldridge's picture
Joined: 2011-09-30
Reputation: 2000

You can model a water-to-air heat pump using PSZ, PVAVS and PVVT by specifying a CONDENSER-TYPE -> WATER-COOLED and attaching a CIRCULATION-LOOP of type CW or WLHP.

Best regards,
Bill