Dear All,
I am modelling VRV unist as PVVT system but PVVT system is
giving lot of unmet hours if i change it to PVV system then my unmet hours
are controlled to the limits so can i go with PVV system for VRV.
Or how can i remove unmet hrs from PVVVT system any suggestions.
Thanks
Sambhav
Hi Sambhav,
Try this option; In detailed data edit mode, pick that particular zone
under "Air-side HVAC Zone parameters" and slightly increase your "Min
design flow". Normally this will be at 0.5 cfm/sq.ft. This will fix the
unmet hours issue.
Thanks
Gopi