Greetings, I have 1320 hrs above cooling throttling range as seen in the BEPS report of the sim file.
However, I am attempting to identify which zone is causing the unmet hours and have been unable to locate the problem zone.
The SS-F report only shows a few zones with a couple few hours unmet, nothing adding up to 1320. And the Air-side Summary Report is showing 0% hrs ouside thrl-range.
I thought there was one something that showed the real unmet hours total in the Space Loads Report somewhere but I am unable to find it.
Thanks for the help.
Kevin
Thanks Brian, SS-R shows a whopping total of 25 unmet hours for all systems.
Kevin
Hi Kevin,
What I like to do is look at the summary tab for each system. If you go to "air-side hvac" and highlight a system in the component tree the select the "summary" tab you will be able to see the space and system total unmet hours for both heating and cooling. By going through each system in the component tree you should be able to identify the problem spaces/system.
Thanks,
Matthew J. Baron, PE
Wendel, 140 John James Audubon Pkwy, Suite 201, Buffalo, NY 14228
p 716.688.0766 f 716.625.6825 e mbaron at wendelcompanies. com w wendelcompanies. com
ARCHITECTURE ENGINEERING PLANNING ENERGY SERVICES CONSTRUCTION MANAGEMENT
CONFIDENTIALITY NOTICE: This email transmission is confidential and is intended only for the person(s) named above. Its contents may also be protected by privilege, and all rights to privilege are expressly claimed and not waived.? If you have received this email in error, please call us immediately and destroy the entire email. If this email is not intended for you, any reading, distribution, copying or disclosure of this email is strictly prohibited.
Please consider the environment before printing this email.
Thanks Matthew, the Air-side Summary Report is showing 0% hrs ouside thrl-range and also has the whopping total of 25 unmet hours as seen in the SS-R report.
Still trying to identify why the BEPS states 1320 unmet hours.
Maybe if I uninstall the program and reinstall it might work.
Kevin
Kevin:
If you could share your .INP and .PD2, it would help us help you.
John R. Aulbach, PE
Thanks Matthew, the Air-side Summary Report is showing 0% hrs ouside thrl-range and also has the whopping total of 25 unmet hours as seen in the SS-R report.?
Still trying to identify why the BEPS states 1320 unmet hours.
Maybe if I uninstall the program and reinstall it might work.
Kevin
Ok guys, thanks for your insight.
Kevin,
It has something to do with your Cooling Design Day. When I change NUMBER-OF-DAYS from 120 to the default (1), the unmet cooling hours goes to down to 11. Cue the Spinal Tap jokes?
Regards,
Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image002.jpg at 01D029C0.70431AD0] [cid:image004.jpg at 01D029C0.70431AD0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com www.pathfinder-ea.com
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.