No heating?

4 posts / 0 new
Last post

Hi all,

I'm running a parametric run to change the time schedule from running 24
hrs to a time schedule (6am to 7pm). For some reason, it won't run the
heating at all. When I check the DOE-2 output (PS-H), heating is zero.
Does anyone have any idea what went wrong? Attached is the file.
Thanks all.

Angelina Kalianda, PE, CEM

Kalianda, Angelina's picture
Joined: 2011-09-30
Reputation: 0

Angelina:
?
I am totally confused.
?
The run you sent has a cooling T-stat schedule of 95 DegF, a heating T-stat schedule of 60, and a fan schedule of always off, unless the heat/cool limts are exceeded.
?
What am?I reading wrong?
?
John Aulbach

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

95 F & 60 F are the hi/lo temps for off hours/night set back. I figured
out the problem. For some reason when I specified hour 1 through 6 and
20 thru 24 to be off in the parametric run, it changes the rest of the
hours to be off as well. I don't know why it does that because it
doesn't always do that in my other file. So I have to actually list all
hours, 1 through 24, to be on or off at the respective hours.

Angelina Kalianda, PE, CEM

Kalianda, Angelina's picture
Joined: 2011-09-30
Reputation: 0

An HTML attachment was scrubbed...