Modeling Ashrae - System 8 in equest - Fan in the parallel box

3 posts / 0 new
Last post

Dear equest users,
According G3.1.3.14 for system 8 the fan parallel box shall be modeled with
0.35 W/cfm fan power.
I was wondering where this paramater can be insered in equest.

In the following screenshot I have input the power of the supply fan.

[image: image.png]

Thank you very much.

Best regards

Konstantina Kalliakoudi
Mechanical Engineer ?.Sc.
www.khmoe.gr

Konstantina Kalliakoudi's picture
Joined: 2019-03-25
Reputation: 0

Konstantina,

You are correct to model VAV systems with parallel and series powered boxes as PIU system type.

This system type will enable several keywords at the zone level on the Airflow tab:
[cid:image003.png at 01D546B7.A30B1670]

Included in these is ZONE-FAN-RATIO and ZONE-FAN-KW/FLOW where you can enter your VAV box fan power.

Footprint

Brian Fountain
Associate
d 416 572 8501 m 416 562 6831

Brian Fountain's picture
Offline
Joined: 2019-05-02
Reputation: 0

For common reference, here are the same inputs when using doe2.3. We have a couple new inputs pertaining to terminal boxes and the fans that love them (ha-ha). These options might merit separate consideration inside/outside the confines of a 90.1 modeling effort:
[cid:image001.png at 01D547BA.174DC700]

[cid:image005.png at 01D515A3.47EDD880]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Energy Performance Contracting
D
M
F
E
913 . 564 . 6361
785 . 410 . 3317
913 . 564 . 6380
nicholas.caton at se.com
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image006.png at 01D515A3.47EDD880]

Nicholas Caton2's picture
Offline
Joined: 2019-03-25
Reputation: 0