High unmet hours when selecting VAV system

4 posts / 0 new
Last post

Hi,

I'm having an issue where I get a very high number of unmet heating hours
with space temps getting down as low as 33F in January.
This is only an issue when I select "Variable Air Volume" system which I
believe is the correct system configuration. It seems like the system is
just failing to heat the space, but I cannot figure out why. Has anyone
has similar issues modeling a VAV system?

Thanks,

mcamp1206's picture
Offline
Joined: 2015-04-07
Reputation: 0

Voila !!
Sounds like you need to have a reheat system defined. That happened to me a few times.
John Aulbach, PE
On Monday, March 12, 2018, 1:33:57 PM PDT, Michael Campbell via Equest-users wrote:

Hi,

I'm having an issue where I get a very high number of unmet heating hours with space temps getting down as low as 33F in January.
This is only an issue when I select "Variable Air Volume" system which I believe is the correct system configuration.? It seems like the system is just failing to heat the space, but I cannot figure out why.? Has anyone has similar issues modeling a VAV system?

Thanks,
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send? a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

Michael,
Have you entered input for HEAT-SET-T? If you leave it blank, you don?t get a main air-handler heating coil.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image007.jpg at 01D3BAB4.618608D0] [cid:image008.jpg at 01D3BAB4.618608D0]

134 South Fitzhugh Street Rochester, NY 14608

T: (585) 698-1956 F: (585) 325-6005

bbishop at pathfinder-ea.com www.pathfinder-ea.com

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.

Bill Bishop's picture
Offline
Joined: 2012-02-25
Reputation: 7

Thanks for the help.
I defined the reheat system and set the thermostat type to Reverse Action
and I was able to get it to work.