Dear All,
I have a constant volume 100% outside air evaporative cooler for a kitchen.
The CFM is 4500. So I set the design flow rate 4500 and outside air flow
4500. When I performed simulation, the simulation was terminated due to
errors. However, there is no error shown in the list of errors. In
addition, if I increase the design flow rate above the outside air flow
rate 4500, then this problem will be gone.
Did anyone have this problem before? How could I fix it?
Thank you!
[image: image.png]
[image: image.png]
[image: image.png]
[image: image.png]
[image: image.png]
Jing Hong
--
School of Architecture and Urban Planning
University of Wisconsin-Milwaukee
An HTML attachment was scrubbed...
URL:
Thank you Brian. It turns out that the supply CFM cannot be smaller than
the exhaust.
Jing
On Mon, Jul 23, 2018 at 8:37 AM Brian Fountain
wrote:
--
PhD Candidate, LEED AP BD+C
School of Architecture and Urban Planning
University of Wisconsin-Milwaukee
Hi Jing,
Your screen shots show that you have entered flowrates for the system supply flow, zonal supply flow, zonal outside air and zonal exhaust flow. The error is caused by the zonal exhaust flow being greater than the entered system supply flow. You have also selected ?Track Exhaust Flow? which requires the air handler to supply at least as much air as the exhaust requirement. You can do any of the following to eliminate the error:
1.) Let the system supply flow rate default (leave the input field empty). The system will be sized to match the zone exhaust flow (or possibly higher).
2.) Enter the system supply flow rate to be at least as much as the zone exhaust flow rate.
3.) Set the zonal exhaust to ?No Airflow Tracking? and the EXHAUST-SOURCE to something other than ?Air Handler?.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005 www.pathfinder-ea.com
bbishop at pathfinder-ea.com
[cid:image004.png at 01D4226F.1E4FFDA0]134 South Fitzhugh Street
Rochester, NY 14608 Ask me why Carbon Fee & Dividend may be right for you.
*****Pathfinder?s Summer Hours begin June 4th. Our switchboard and office will be closed at noon on Fridays through August 31st.****
Thank you Bill. I revised the exhaust flow rate setting based on your
advise, and it works!
Jing
On Mon, Jul 23, 2018 at 9:22 AM Bishop, Bill
wrote:
--
PhD Candidate, LEED AP BD+C
School of Architecture and Urban Planning
University of Wisconsin-Milwaukee
Bill,
I like to compliment you on your very useful diagnosis and explanation of the problem.?
Well done!
Joe