To clarify, my zones are not cooled (no cooling schedules, i.e. no set point for cooling to be met, my zone cooling loads are ignored). The system has a cooling coil that is sized to take the dehumidification load only. The system does not attempt to maintain a maximum temperature in the zone.
[Bouthillette Parizeau]
Jason Ng_ing. M.Sc.A.
jng at bpa.ca | t: 5143833747x2813
De : Porter, Frederick NOR [mailto:fporter at noresco.com]
Envoy? : 7 juin 2017 10:46
? : Ng, Jason ; equest-users at lists.onebuilding.org
Objet : RE: Dehumidification issue - REPOST
Jason,
You state that this "system" will "dehumidify air only (no cooling..." Exactly HOW does it dehumidify, if not by cooling and condensation?
Fred
Your ZONES are COOLED. By the mixed air delivered to them from the AHU, even if that cooling effect is not ?controlled? zone by zone. Hence the term economizer COOLING. Your ?zone cooling loads? are not ignored. They reheat the air to a balance point zone temperature, and if that temperature is less than the heating setpoint, whatever zone heating exists should turn on.
It?s not clear how the mixed air temps, and economizer, and supply air temps are controlled in the real system, which will result in more or less cooling from the central air. In eQUEST, a central AHU will snap into overcool-reheat mode when the RA humidity exceeds the limit. It may be difficult to get the PVAVS AHU to NOT turn on the cooling coil for anything except dehumidification. Various combinations of cooling control settings might get close. If you try to use ?WARMEST? SAT reset, that may require zone cooling setpoints, even if those don?t affect any flows. eQUEST only uses the return air RELATIVE humidity to snap into overcooling, so if the zone temperatures vary from typical, the model dehumidification may not be controlled much like the actual dehumidification.
IF the AHU uses hot gas reheat during dehumidification, that can?t be input directly in my version of eQ, it needs to be input as a parametric component; ?HVAC System?/?Cooling Condenser?/?Max Condenser Recovery?
Jason, I think one mix-up may be the lingo - if the zones or supply air have heat removed, then it is being cooled even if the cooling is provided for dehumidification purposes, or if the economizer is operating and the zones are cooled as a byproduct of dehumidification.
Where is the 60% RH setpoint entered? The system could still supply lower humidity air to the spaces in order to maintain RH in the zones. I don't see why this would require the coil to operate though, unless the packaged system requires one control zone that has a temperature control schedule. If none was provided is one made by default?
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
You say the system will snap into overcool-reheat mode when RA humidity exceeds the limit. However according to my hourly results, my return air humidity ratio and mix air humidity ratio NEVER surpass my maximum humidity set point, yet I still have loads on my cooling coil during the summer, and moisture removed from the airstream.
What else would be activating the cooling if its not my zones or my max humidity set point?
[Bouthillette Parizeau]
Jason Ng_ing. M.Sc.A.
jng at bpa.ca | t: 5143833747x2813
De : Porter, Frederick NOR [mailto:fporter at noresco.com]
Envoy? : 7 juin 2017 13:24
? : Ng, Jason ; equest-users at lists.onebuilding.org
Objet : RE: Dehumidification issue - REPOST
Your ZONES are COOLED. By the mixed air delivered to them from the AHU, even if that cooling effect is not "controlled" zone by zone. Hence the term economizer COOLING. Your "zone cooling loads" are not ignored. They reheat the air to a balance point zone temperature, and if that temperature is less than the heating setpoint, whatever zone heating exists should turn on.
It's not clear how the mixed air temps, and economizer, and supply air temps are controlled in the real system, which will result in more or less cooling from the central air. In eQUEST, a central AHU will snap into overcool-reheat mode when the RA humidity exceeds the limit. It may be difficult to get the PVAVS AHU to NOT turn on the cooling coil for anything except dehumidification. Various combinations of cooling control settings might get close. If you try to use "WARMEST" SAT reset, that may require zone cooling setpoints, even if those don't affect any flows. eQUEST only uses the return air RELATIVE humidity to snap into overcooling, so if the zone temperatures vary from typical, the model dehumidification may not be controlled much like the actual dehumidification.
IF the AHU uses hot gas reheat during dehumidification, that can't be input directly in my version of eQ, it needs to be input as a parametric component; "HVAC System"/"Cooling Condenser"/"Max Condenser Recovery"
To go back to Jason?s original specific questions:
1. How does eQUEST control the maximum humidity allowed in the supply airstream?
There is direct control of humidity in the supply airstream. Humidity is controlled by the ?system? RH, which is really a return air RH.
2. How could one possibly explain a cooling load/consumption without any cooling set point schedules in any of the zones supplied by my system and zero moisture removed from the air?
In a SINGLE ZONE system, the supply air temperature is controlled to meet zone temperature setpoint schedules. In a VAV/PIU, PVAV, CVRH system, i.e. the type of system you say you are modeling, the supply air is controlled in a variety of ways, but the simplest, and eQUEST default, is a constant 55F AHU ?SAT?, i.e., discharge air temperature. If the MAT > SAT ? fan dT, there will be a cooling load on the coil. If the MA WBT < SAT, which might be the case in your location, there can be sensible cooling w/o any condensation.
Oops, meant to write that there is NOT direct control of humidity in supply air. That is, you can?t specify a coil leaving max RH of 80%, or something like that, which someone might put in a sequence, in lieu of some other measurement/control point.
Also in a VAV system the decrease in SAT called for by exceeding the system max RH setpoint can only happen if the current hour?s SAT > MIN-SUPPLY-T.
Also, I assume the ?VAV? minimum flows are set to 100% everywhere in your modeled system. In a VAV system, what the ZONE cooling setpoint schedule really controls is the airflow modulation. As the zone temp increases through the throttling range around the hour?s cooling setpoint, the zone airflow increases from minimum to 100%. W/o a cooling setpoint, this increase never happens. If the minimum airflows are at 100%, then the cooling setpoint SHOULD do nothing, unless it is being referenced by a WARMEST reset control.
Fred
MIN-SUPPLY-T
For systems that can provide cooling, this is a required keyword that gives the minimum temperature of the air delivered to the zone. MIN-SUPPLY-T and COOL-DESIGN-T are used to size the capacity of the cooling coil and supply air flow rate. The supply air flow rates needed to satisfy the heating and cooling requirements are compared and the greater of the two quantities is used for the system air flow rate. Note that MIN-SUPPLY-T also controls the amount of moisture that can be removed by the cooling coils.
Note, that for those systems that are to maintain a constant cooling air discharge temperature (see keyword COOL-CONTROL), the control set point is determined by the value entered for COOL-SET-T rather than MIN-SUPPLY-T. In this case, the program uses MIN-SUPPLY-T to limit subcooling for dehumidification purposes (and to calculate the design air flow rate for cooling).
Note that MIN-SUPPLY-T is the design supply temperature at the zone, downstream of duct losses. COOL-SET-T, COOL-SET-SCH, COOL-RESET-SCH and the heating counterparts are all defined as entering the duct, upstream of duct losses. As such, they should be adjusted for the expected duct losses so that the hourly supply temperature at the zone is the desired temperature.
COOL-SET-T
The cooling air supply temperature setpoint when COOL-CONTROL = CONSTANT. Note that even though COOL-SET-T determines the cooling air supply temperature, the program uses MIN-SUPPLY-T to calculate the design supply air flow rate.
Note that MIN-SUPPLY-T is the design supply temperature at the zone, downstream of duct losses. COOL-SET-T, COOL-SET-SCH, COOL-RESET-SCH and the heating counterparts are all defined as entering the duct, upstream of duct losses. As such, they should be adjusted for the expected duct losses so that the hourly supply temperature at the zone is the desired temperature. They should also be reduced by one-half of the COOL-CTRL-RANGE.
Hi Frederick,
To clarify, my zones are not cooled (no cooling schedules, i.e. no set point for cooling to be met, my zone cooling loads are ignored). The system has a cooling coil that is sized to take the dehumidification load only. The system does not attempt to maintain a maximum temperature in the zone.
[Bouthillette Parizeau]
Jason Ng_ing. M.Sc.A.
jng at bpa.ca | t: 5143833747x2813
De : Porter, Frederick NOR [mailto:fporter at noresco.com]; equest-users at lists.onebuilding.org
Envoy? : 7 juin 2017 10:46
? : Ng, Jason
Objet : RE: Dehumidification issue - REPOST
Jason,
You state that this "system" will "dehumidify air only (no cooling..." Exactly HOW does it dehumidify, if not by cooling and condensation?
Fred
Your ZONES are COOLED. By the mixed air delivered to them from the AHU, even if that cooling effect is not ?controlled? zone by zone. Hence the term economizer COOLING. Your ?zone cooling loads? are not ignored. They reheat the air to a balance point zone temperature, and if that temperature is less than the heating setpoint, whatever zone heating exists should turn on.
It?s not clear how the mixed air temps, and economizer, and supply air temps are controlled in the real system, which will result in more or less cooling from the central air. In eQUEST, a central AHU will snap into overcool-reheat mode when the RA humidity exceeds the limit. It may be difficult to get the PVAVS AHU to NOT turn on the cooling coil for anything except dehumidification. Various combinations of cooling control settings might get close. If you try to use ?WARMEST? SAT reset, that may require zone cooling setpoints, even if those don?t affect any flows. eQUEST only uses the return air RELATIVE humidity to snap into overcooling, so if the zone temperatures vary from typical, the model dehumidification may not be controlled much like the actual dehumidification.
IF the AHU uses hot gas reheat during dehumidification, that can?t be input directly in my version of eQ, it needs to be input as a parametric component; ?HVAC System?/?Cooling Condenser?/?Max Condenser Recovery?
Good luck.
Fred
Jason, I think one mix-up may be the lingo - if the zones or supply air have heat removed, then it is being cooled even if the cooling is provided for dehumidification purposes, or if the economizer is operating and the zones are cooled as a byproduct of dehumidification.
Where is the 60% RH setpoint entered? The system could still supply lower humidity air to the spaces in order to maintain RH in the zones. I don't see why this would require the coil to operate though, unless the packaged system requires one control zone that has a temperature control schedule. If none was provided is one made by default?
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
Hi Fred,
You say the system will snap into overcool-reheat mode when RA humidity exceeds the limit. However according to my hourly results, my return air humidity ratio and mix air humidity ratio NEVER surpass my maximum humidity set point, yet I still have loads on my cooling coil during the summer, and moisture removed from the airstream.
What else would be activating the cooling if its not my zones or my max humidity set point?
[Bouthillette Parizeau]
Jason Ng_ing. M.Sc.A.
jng at bpa.ca | t: 5143833747x2813
De : Porter, Frederick NOR [mailto:fporter at noresco.com]; equest-users at lists.onebuilding.org
Envoy? : 7 juin 2017 13:24
? : Ng, Jason
Objet : RE: Dehumidification issue - REPOST
Your ZONES are COOLED. By the mixed air delivered to them from the AHU, even if that cooling effect is not "controlled" zone by zone. Hence the term economizer COOLING. Your "zone cooling loads" are not ignored. They reheat the air to a balance point zone temperature, and if that temperature is less than the heating setpoint, whatever zone heating exists should turn on.
It's not clear how the mixed air temps, and economizer, and supply air temps are controlled in the real system, which will result in more or less cooling from the central air. In eQUEST, a central AHU will snap into overcool-reheat mode when the RA humidity exceeds the limit. It may be difficult to get the PVAVS AHU to NOT turn on the cooling coil for anything except dehumidification. Various combinations of cooling control settings might get close. If you try to use "WARMEST" SAT reset, that may require zone cooling setpoints, even if those don't affect any flows. eQUEST only uses the return air RELATIVE humidity to snap into overcooling, so if the zone temperatures vary from typical, the model dehumidification may not be controlled much like the actual dehumidification.
IF the AHU uses hot gas reheat during dehumidification, that can't be input directly in my version of eQ, it needs to be input as a parametric component; "HVAC System"/"Cooling Condenser"/"Max Condenser Recovery"
Good luck.
Fred
To go back to Jason?s original specific questions:
1. How does eQUEST control the maximum humidity allowed in the supply airstream?
There is direct control of humidity in the supply airstream. Humidity is controlled by the ?system? RH, which is really a return air RH.
2. How could one possibly explain a cooling load/consumption without any cooling set point schedules in any of the zones supplied by my system and zero moisture removed from the air?
In a SINGLE ZONE system, the supply air temperature is controlled to meet zone temperature setpoint schedules. In a VAV/PIU, PVAV, CVRH system, i.e. the type of system you say you are modeling, the supply air is controlled in a variety of ways, but the simplest, and eQUEST default, is a constant 55F AHU ?SAT?, i.e., discharge air temperature. If the MAT > SAT ? fan dT, there will be a cooling load on the coil. If the MA WBT < SAT, which might be the case in your location, there can be sensible cooling w/o any condensation.
Oops, meant to write that there is NOT direct control of humidity in supply air. That is, you can?t specify a coil leaving max RH of 80%, or something like that, which someone might put in a sequence, in lieu of some other measurement/control point.
Also in a VAV system the decrease in SAT called for by exceeding the system max RH setpoint can only happen if the current hour?s SAT > MIN-SUPPLY-T.
Also, I assume the ?VAV? minimum flows are set to 100% everywhere in your modeled system. In a VAV system, what the ZONE cooling setpoint schedule really controls is the airflow modulation. As the zone temp increases through the throttling range around the hour?s cooling setpoint, the zone airflow increases from minimum to 100%. W/o a cooling setpoint, this increase never happens. If the minimum airflows are at 100%, then the cooling setpoint SHOULD do nothing, unless it is being referenced by a WARMEST reset control.
Fred
MIN-SUPPLY-T
For systems that can provide cooling, this is a required keyword that gives the minimum temperature of the air delivered to the zone. MIN-SUPPLY-T and COOL-DESIGN-T are used to size the capacity of the cooling coil and supply air flow rate. The supply air flow rates needed to satisfy the heating and cooling requirements are compared and the greater of the two quantities is used for the system air flow rate. Note that MIN-SUPPLY-T also controls the amount of moisture that can be removed by the cooling coils.
Note, that for those systems that are to maintain a constant cooling air discharge temperature (see keyword COOL-CONTROL), the control set point is determined by the value entered for COOL-SET-T rather than MIN-SUPPLY-T. In this case, the program uses MIN-SUPPLY-T to limit subcooling for dehumidification purposes (and to calculate the design air flow rate for cooling).
Note that MIN-SUPPLY-T is the design supply temperature at the zone, downstream of duct losses. COOL-SET-T, COOL-SET-SCH, COOL-RESET-SCH and the heating counterparts are all defined as entering the duct, upstream of duct losses. As such, they should be adjusted for the expected duct losses so that the hourly supply temperature at the zone is the desired temperature.
COOL-SET-T
The cooling air supply temperature setpoint when COOL-CONTROL = CONSTANT. Note that even though COOL-SET-T determines the cooling air supply temperature, the program uses MIN-SUPPLY-T to calculate the design supply air flow rate.
Note that MIN-SUPPLY-T is the design supply temperature at the zone, downstream of duct losses. COOL-SET-T, COOL-SET-SCH, COOL-RESET-SCH and the heating counterparts are all defined as entering the duct, upstream of duct losses. As such, they should be adjusted for the expected duct losses so that the hourly supply temperature at the zone is the desired temperature. They should also be reduced by one-half of the COOL-CTRL-RANGE.