eQUEST Detailed Reports: Heating Equipment Efficiency Included in Space Heating & Maximum Heating Load Values?

3 posts / 0 new
Last post

Does anyone know if the "Space Heating" value in MBtu/y found on the "Building Energy Performance Summary" includes the heating equipment efficiency? Or is it calculated without including the heating system equipment efficiency?

Also, does the "Maximum Heating Load" in kBtu/y found on the "Building HVAC Load Summary" include the heating equipment efficiency?

Thank you.

Sandy

Sandra LaFlamme, PE, CEM

Sandy LaFlamme's picture
Offline
Joined: 2012-02-17
Reputation: 0

hi sandy please forgive my phone texting challenges.

bothe the beps and the bepu are absolute end use site energy, that which would appear on an energy bill. contains allefficiency and ancillary lolads.

max space heating lolad is exactlt that,,,load.

hope that helps.

john r. aulbach, pe

----------
Sent from AT&T's Wireless network using Yahoo! Mail

------Original Message------
From: Sandy LaFlamme To: "'equest-users at lists.onebuilding.org'" Date: Monday, November 18, 2013 9:37:39 AM GMT-0500
Subject: [Equest-users] eQUEST Detailed Reports: Heating Equipment Efficiency Included in Space Heating & Maximum Heating Load Values?

Does anyone know if the "Space Heating" value in MBtu/y found on the "Building Energy Performance Summary" includes the heating equipment efficiency? Or is it calculated without including the heating system equipment efficiency?

Also, does the "Maximum Heating Load" in kBtu/y found on the "Building HVAC Load Summary" include the heating equipment efficiency?

Thank you.

Sandy

Sandra LaFlamme, PE, CEM | Engineering

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

Thank you John, I appreciate the prompt response and the information is much appreciated!!

Thanks again,
Sandy

Sandy LaFlamme's picture
Offline
Joined: 2012-02-17
Reputation: 0