Any suggestions as to how to make the DHW heater a condensing boiler ?? The Condensing feature is for a boiler , which wants a Hot Water loop, NOT a DHW loop..
John R. Aulbach, PE, CEM
Hi John,
This may get you started:
- Create a HW Loop
- Create a Condensing Boiler/Pump, attach to the new loop
- Define a process load + schedule in the second tab of the loop to match your DHW consumption. You may need to define the load with MBtu/h and not gpm.
- As a result you should see your condensing DHW pop up in the consumption reports as a green process load on the gas side.
- You might want to leave your normal DHW loop in operation while setting this up as a check to see that you're matching well before deleting. Review the HW loop/boiler inputs carefully to ensure everything is appropriate to DOMHW.
Screengrabs follow to illustrate the concept:
[cid:image003.png at 01CD283F.ED4DEC10]
[cid:image002.png at 01CD2840.AFDAEA30]
Best of luck!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
John,
You could also model a condensing DHW boiler as any other gas DHW heater, but with a custom HIR-FPLR performance curve and a better full load HIR. Part load efficiency is published for several models of condensing DHW boilers. Remember to normalize the custom performance curve to 1.0 at full load.
Regards,
Bill