A 50,000 sf building we are looking at has electric DX cooling and electric heat VAV terminal boxes in the zones. The only gas use in this system is for a small pre-heat coil on the RTU and there is also an energy recovery ventilator. In developing the Baseline model, should we use System 5 (gas boiler) or go with System 6 (all electric)?
With gas, I know the default is to use Sys 5 but in this case the pre-heat is a very small part of the system so the "predominant" heating energy use is electric. The Baseline will still be modeled with the same gas pre-heater per Appendix G, either way.
Many thanks for your thoughts.
Regards,
Jeff Ross-Bain, PE, LEED Fellow
President
404-220-8955
www.rbgb.com
Build Green. Save Time. Save Money.
Not sure which version you are looking at, but I believe you will need to
go with a Appendix G System 5, sorry. That is officially considered a
Fossil/Electric Hybrid system, not a preheat coil. See this ASHRAE
interpretation for 90.1-2007:
https://www.ashrae.org/File%20Library/docLib/StdsInterpretations/IC-90-1-2007-15.pdf
If you are looking at newer versions, there might be a more recent ASHRAE
interpretation - worth investigating, but unlikely to have a different
outcome based on their previous interpretation.