Does anyone know how to activate/install Floor Panel Heat (panel heating elements) in the Zone-Heating screen?
Thank you,

Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513

Paul Diglio's picture
Offline
Joined: 2011-09-30
Reputation: 400

Paul,
The Help documentation says it?s not implemented in DOE2.3. Using DOE2.2, you can use panel heating elements if the zone is assigned to a Floor Panel Heating system (TYPE = FPH; shows as ?Radiant Slab? in the system drop-down menu). I suggest modeling the panel heating as baseboards and then figuring out how to add heat losses if you think that?s needed.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer

[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com www.pathfinder-ea.com
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image005.png at 01D5CAEF.945E9A40] Ask me why Carbon Fee & Dividend may be right for you.

Bill Bishop's picture
Offline
Joined: 2012-02-25
Reputation: 7

As always, thanks for the help Bill.

Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513

On Tuesday, January 14, 2020, 3:34:05 PM EST, Bishop, Bill wrote:

Paul,

The Help documentation says it?s not implemented in DOE2.3. Using DOE2.2, you can use panel heating elements if the zone is assigned to a Floor Panel Heating system (TYPE = FPH; shows as ?Radiant Slab? in the system drop-down menu). I suggest modeling the panel heating as baseboards and then figuring out how to add heat losses if you think that?s needed.

Regards,

~Bill

?

William Bishop, PE, BEMP, BEAP, CEM, LEED AP

Senior Energy Engineer

?

T: (585) 698-1956????????????? ??????????F: (585) 325-6005

bbishop at pathfinder-ea.com????????www.pathfinder-ea.com

134 South Fitzhugh Street

Rochester, NY 14608?????????????????????Ask me why Carbon Fee & Dividend may be right for you.

?

Paul Diglio's picture
Offline
Joined: 2011-09-30
Reputation: 400