ERV Output

3 posts / 0 new
Last post

I have created a simulation with an energy recovery ventilator/cooling
unit. I cannot figure out where the supply/exhaust fan power is shown on
the output reports. I would expect it to be a part of the SV-A report for
the system, however the total KW I input is not reflected in the kW output.

Caleb Freeman's picture
Offline
Joined: 2012-02-09
Reputation: 0

The ERV output is a separate report called ERV Energy Recovery Summary.
You should be able to find this located after the SS-P and SS-Q reports,
or just
Ctrl+F and search for ERV.

Umesh Atre's picture
Offline
Joined: 2011-09-30
Reputation: 0

ERV fan power is not included in the SV-A. It is included in the ERV
report as stated below. It is included in fan energy in the BEPS, PS-E
etc. reports.