RE: Detailed Report, LS-F Building Monthly Load Components

Why would roof heat losses be zero in a model defined with plenum spaces
that have roofs components? In report LS-F, there are no losses reported
in 'Roof' and 'Wall' heat losses seem exceptionally high, as if 'Roof'
losses are reported in 'Walls'.

All spaces were created using the eQuest wizard mode. Inspecting the
"exterior surface properties", the word "Roof" appears below the surface
name. All roof constructions are made with layers input, having a
U-Value 0f 0.043. When creating exterior surfaces in detailed edit mode,
no option exists for defining an exterior surface as a roof or wall.

So, how are the loads associated with roofs reporting in LS-F? What
other reasons might roof loads not report, or at least not report in the
correct load component?

Jonathan R. Smith AIA LEED(r)AP

Jonathan Smith's picture
Offline
Joined: 2011-09-30
Reputation: 0

An HTML attachment was scrubbed...
URL:

Bruce Easterbrook's picture
Joined: 2011-09-30
Reputation: 0

Hi Bruce:

Thanks you for your reply.

The LS-F report I'm reviewing is a building wide report which should be
inclusive of all spaces. As stated previously, MBTUs through ROOF
components is listed as zero. However, the space level report (LS-E) for
the one of the plenums with a roof component shows heat loss of the roof
component. This is true for some of the other plenum spaces. Any ideas
why the space level report (LS-E) ROOF components are not reported on
the building wide report (LS-F) as roof components?

Jonathan

Jonathan Smith's picture
Offline
Joined: 2011-09-30
Reputation: 0

An HTML attachment was scrubbed...
URL:

Bruce Easterbrook's picture
Joined: 2011-09-30
Reputation: 0

For what it's worth, the example LS-F report in the help file
documentation also shows only 0's in the roof component. From within
eQuest, go to the Help menu, select DOE-2 Help. Expand the "Volume 4:
Libraries & Reports" and then the "Reports" topics. LS-E and LS-F are
under the loads reports. The text says the monthly space components are
summed across spaces. The definition of the LS-F report excludes plenum
spaces:

This report gives a breakdown of loads on a monthly basis for the entire
building, according to the source of the load. The loads in
unconditioned spaces (ZONE-TYPE = UNCONDITIONED or PLENUM) are not
included; all entries are in millions of Btu/month.

This just explains why they don't show up in the LS-F...I believe that
the mechanism used by eQuest to account for heat gain in the plenums is
to apply that heat gain to the return air before the system, thereby
increasing temperature, humidity, etc. in the RA stream due to the loads
in the plenum spaces connected to a given system. Someone from Hirsch
can jump in if I got that wrong.

I'm curious if anyone else has dug deeper on this than I have, though?

Jeremy R. Poling, PE, LEED AP+BDC

Jeremy Poling2's picture
Offline
Joined: 2011-09-30
Reputation: 0

An HTML attachment was scrubbed...
URL:

Bruce Easterbrook's picture
Joined: 2011-09-30
Reputation: 0

Hey everyone,

Sorry to chime in late... but I have some input to wedge into the
conversation as it's wrapping up:

First: As has already been said, LS-F is inclusive of all 'conditioned'
spaces. I didn't realize the DOE2 entries explicitly (more or less) say
that, and had figured it out for myself via logic/gray hair growth... =)
I'll take this as a reminder that the DOE2 help files are perpetually
more useful than they may seem!

Second: I'm also no developer, but Bruce's conclusions didn't sit well
with me so I did a quick study to confirm... I don't think you can
characterize plenum loads as being *entirely* separated from the
conditioned spaces... Do such loads (really hot/cold plenums) get
directed straight back to the central air handler, or do they also
partially interact with the zones as well?

I know ceilings generated by eQuest wizards by default are not
adiabatic, but do use a construction with defined heat transmittance
properties.

I slapped together a 1-zone, 1-floor dummy model and tried changing the
default ceiling construction (U~0.5) to adiabatic in a parametric run.
Return air path was set to "plenum zones." The plenum zone itself was
changed from "unconditioned" to "plenum:"

Lo and behold: The two runs do indeed have differing
cooling/heating/ventilation consumptions (attached)!

* Investigation of the LS-F reports shows the whole building
deals with identical load components altogether - which is expected.

* Comparing of the LS-E reports reveals the plenum with an
adiabatic ceiling has less heating and less cooling to deal with over
the year. Both runs' conditioned space however deal with identical
loads for each month.

Conclusions!

1. Bruce is NOT to be questioned: Plenums modeled as a return air
path do not transmit their loads to the corresponding spaces below.
They carry their loads directly to the parent system.

2. Return air plenums DO however receive heating/cooling loads
transmitted from the conditioned spaces below via the ceiling surfaces.
It's basically a 1-way street.

3. I'd agree real-world behavior is somewhere in-between:
Return-air plenum ceilings should act as a 2-way street thermally, and a
single plenum can be hot on one side but cold on another at any given
instance. In many cases however, I suspect the assumption of all loads
staying in the plenum is closer to reality than assuming they all dump
into the corresponding space below, from an supply airflow-sizing
perspective.

~Nick

NICK CATON, P.E.

Nick-Caton's picture
Offline
Joined: 2011-09-30
Reputation: 805

eQuesters:

I ran an hourly report comparing zone temperatures for a plenum and
adjacent zone. Temperature delta for the plenum was on average 4 degrees
less in winter than the occupied zone. I could not identify a System or
Zone hourly report variable to track heat flux of interior surfaces.

Looking at the DOE 2.1 Engineering Manual there is an explanation of the
calculation procedure whereby the LOADS program temperatures are
adjusted in the SYSTEMS program to account for a delta between adjacent
zones. This adjusted load impacts the system sizing when the user
selects "ADJUST-LOADS".

IV.25-26, Calculation Outline, A.

IV.174-185, Interface between LOADS and SYSTEMS (Subroutine TEMDEV)

Jonathan