Equest and Heat Pump

2 posts / 0 new
Last post

Hello to all equest users,

I was wondering, can I assign a Hot Water Loop with a Heat Pump?

As I see there only Electric boiler available.

Thank you

Konstantina Kalliakoudi

Mechanical Engineer,M.Sc., LEED AP

KHM

Filolaou 28, Ilioupoli, Athens, Greece

Tel. 0030 210 99 69 680

www.khmoe.gr

Konstantina Kalliakoudi's picture
Joined: 2019-03-25
Reputation: 0

Hi Konstantina,
If I understand your question, you want to use a water-to-water or air-to-water heat pump to provide hot water. You can model this using a heat pump chiller (a CHILLER with TYPE=HEAT-PUMP). You can only assign a single loop for the heat pump chiller load, and the keyword and eQUEST drop-down input is for a CHW-LOOP, but it accepts both CHW and 2-Pipe loops. You have to assign a heat pump chiller to a 2-Pipe loop for it to provide heating. You can configure the 2-Pipe loop to operate the same as a Hot Water loop if you want, by setting the LOOP-OPERATION to SNAP or SCHEDULED and using a high snap temperature. Then you would only assign hot water loads to the 2-Pipe loop.
Regards,
~Bill