Demand Direct Process Load

3 posts / 0 new
Last post

Hi,
I'm modeling a building for LEED, but when I go to equest LEED report I notice that my direct process load for demand is not equal, anyone know why this happen?

I review the rate and the schedules and are the same also the energy load is the same for the proposed and the baseline.

Thanks,
Ing. Juan Carlos Sanabria F.
Tel.: (506) 2256-7020
Fax: (506) 2256-5608
From USA: 1-305-433-3668
Calle 30, Avenida 0 y 2. San Jos?, Costa Rica

[Logo CTS firma]
Este correo puede contener informaci?n protegida por el secreto profesional. Si usted no es la persona a quien va dirigido, por favor tome en cuenta que su divulgaci?n, distribuci?n o reproducci?n es estrictamente prohibida. Cualquier persona que reciba este mensaje por error debe notificarlo inmediatamente al remitente v?a telef?nica o correo electr?nico y borrarlo permanentemente de su computador. Los comentarios plasmados en este correo son del remitente solamente y no reflejan necesariamente la posici?n de CTS S.A.
Por favor considere su responsabilidad con el medio ambiente antes de imprimir este correo electr?nico
----------------------------------------------------------------------------------------------------------------
This mail may contain information that is legally privileged, confidential or exempt from disclosure. If you are not the intended recipient, please note that any dissemination, distribution or copying of this message is strictly prohibited. Anyone who receives this message in error should notify the sender immediately by telephone or by e-mail and delete it permanently from their computer. The opinions above are those of the author and do not necessarily reflect the position of CTS S.A.
Please consider your environmental responsibility before printing this e-mail

Juan Sanabria's picture
Offline
Joined: 2014-08-06
Reputation: 0

Is the process load on a hot water or chilled water loop? I think these are
dependent a little on the overall loop temp/load and are never same for
different runs. If it just an internal load, then look at the schedule also
to make sure that is same.
-Rohini

R B's picture
R B
Offline
Joined: 2011-09-30
Reputation: 4

Double check the timing of the peaks - the graphical presentation in eQUEST is the coincident peak - the contribution of each component at the time that the building hits its total highest demand.

It's likely that the proposed building has a peak later in the day due to one or more efficiency measures that are included. If the process loads are lower at this time, the graphical presentation will show that the peak component is less than the baseline case. (Or if the process ramps up later in the day, it could be more?)

You'll need to go into the *.SIM file to get the reported peaks for the process loads (and show the annual totals to also be the same) to demonstrate that the schedules are consistent, or otherwise explain to the reviewer what is happening.

David

David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates

David Eldridge's picture
Offline
Joined: 2012-05-08
Reputation: 1