I've modeled a nine story office building which requires different
shells for several of the levels in the building. It also has a nine
story (full height) atrium that will be used to extract all of the
exhaust air (i.e. supply OA to the floors and condition via FC units
and pull exhaust air out of the top of the atrium). I'm aware that
eQuest doesn't track air flows but I'd like to best approximate the
atrium effects on the overall energy use of the building.

Current approach: I've modeled each floor as a separate zone and I'm
going to delete the floors and turn the ceilings into air-walls and
link them to the zone above. Currently I'm conditioning all of the
zones that make up the atrium but at some point I'd like to explore
not conditioning these zones to more accurately approximate how we'd
run the building.

Comments?

One alternate approach I've seen proposed is to replace all nine zones
in the atrium with one full height zone - the advantage is the glass
on the roof and upper walls can "see" the floor and walls in all of
the zones of the atrium. However this won't let me later go back in
and explore any variation of temperature with height. I think this
might be important as I would expect the air at the top of the atrium
to be warmer and cause more load on the top floor zones next to the
atrium.

--
Jason Quinn

JasonQuinn's picture
Offline
Joined: 2012-03-03
Reputation: 0

Sounds like a task that would be better done with single zone and analysed
using CFD to me..
Possibly use a CFD program then use insight to work around your Equest
model..

*Jeremiah D. Crossett*

CleanTech Analytics's picture
Joined: 2012-02-09
Reputation: -1

If CFD isn't an option, one other eQuest option would be to break the atrium up into one conditioned, and one or more plenums (TYPE = PLENUM, not UNCONDITIONED). Make an assumption about how much load is displaced or only present in the plenum portion of the atrium. Then, put a portion of the glazing and loads in the plenum(s). You might for example assume that the bottom two floors are one conditioned zone, and the top seven floors are a large plenum. I believe the air in the plenum should pick up the heat from the glazing and loads placed in it. I would be cautious about using eQuest to predict what will actually happen in an atrium though.
Jeremy

___________________________________________
Jeremy McClanathan, P.E., BEMP, HFDP, LEED(r) AP BD+C

Jeremy McClanathan's picture
Joined: 2011-09-30
Reputation: 200

Hi Jason,

Another alternative is to model the lowest floor level of the atrium as a
conditioned space, and the upper 8 storey part of the atrium as a return
plenum.

Shaun Martin LEED AP

sm
Shaun Martin's picture
Offline
Joined: 2011-09-30
Reputation: 0