Breaking out fan power from EER & COP?

3 posts / 0 new
Last post

Hi - Can someone point me towards a reference that details how to break
the fan power out of the EER & COP ratings in the 6.8.1 tables in 90.1?
Specifically, I need the relationship between the EER & COP for PTHP in
6.8.1D with and without fan power included. Thanks.

Morgan Heater, P.E. BEMP, LEED AP

Morgan Heater's picture
Offline
Joined: 2011-10-02
Reputation: 0

Check out page G-26 in the User's Manual for ASHRAE 90.1-2004 and example
G-G - Calculating COP for Compressor and Condenser...

Shruti Kasarekar's picture
Joined: 2011-10-02
Reputation: 0

Hi Morgan,
California's Non-Residential ACM also has a good approach. Comnet
probably does as well, but I'm not as familiar with that doc.

http://www.energy.ca.gov/title24/2008standards/nonresidential_manual.html

*Aleka Pappas, P.E., LEED AP*

Aleka Pappas3's picture
Offline
Joined: 2011-09-30
Reputation: 0