Difference between fan energy consumption almost same using constant speed and variable speed fan control

4 posts / 0 new
Last post

Hi all,

I am working on the project where the project space is served by chilled
water to meet the building heat load. And in eQuest, I have considered the
single zone Reheat system under the Air Side HVAC tab for AHU having 14200
CFM working 9 hours 6 days a week.

My doubt is that whether I set the fan controls constant speed or variable
speed, the software generated fan energy consumption KWh are nearly the
same (only a difference of 16 KWh) between both the cases.

This seems that I will not get the benefit of variable speed fan control in
case there is a VFD equipped to AHU.

Can anyone help me why there is a very little difference in fan energy
consumption using constant speed and variable speed fan in the model.

Nitin Harjai's picture
Offline
Joined: 2015-09-23
Reputation: 0

Dear Nitin,

You can change the system type like VAV system and it will give you savings
of VFD speed. In eQuest single zone reheat with vfd option is allow to take
vfd speed savings.

Thanks
Anil
??-

On Sun, 18 Oct 2020 at 9:52 PM, Nitin Harjai via Equest-users <

Anil Jangid's picture
Offline
Joined: 2019-05-16
Reputation: 0

Hi Nitin:
If you set the system to single zone reheat, you have nothing to vary the airflow (VAV). So the fan tab should basically show the same fan kWh regardless of constant speed or variable speed. You need to have a system that will vary the airflow before you can set fan speed at variable.
Hope this helps.
John R Aulbach, PE
On Sunday, October 18, 2020, 09:22:03 AM PDT, Nitin Harjai via Equest-users wrote:

Hi all,
I am working on the project where the project space is served by chilled water to meet the building heat load. And in eQuest, I have considered the single zone Reheat system under the Air Side HVAC tab for AHU having 14200 CFM working 9 hours 6 days a week.
My doubt is that whether I set the fan controls constant speed or variable speed, the software generated fan energy consumption KWh are nearly the same (only a? difference of 16 KWh) between both the cases.
This seems that I will not get the benefit?of variable speed fan control in case there is a VFD equipped to AHU.
Can anyone help me why there is a very little difference in fan energy consumption using constant speed and variable speed fan in the model.?

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send? a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

John Aulbach's picture
Offline
Joined: 2011-09-30
Reputation: 1

Hi Nitin,
You have to set the MIN-FLOW-RATIO to something less than 1 in order for the system to run at lower flowrate to get VFD fan energy savings. The MIN-FLOW-RATIO default is 1 and does not automatically change with selection of FAN-CONTROL. (However, the default for FAN-CONTROL changes to variable speed if the MIN-FLOW-RATIO is less than 1.)
Regards,
~Bill