Hi folks,

i have a question for you.

Comparing the ?REPORT ? SS-D Building
HVAC Load Summary? with the ?REPORT ? LS-D Building Monthly Loads Summary? I?
ve noticed that the values of heating and cooling energy are different between
the two reports. Why it?s happen? What?s the difference between the two
reports?

Thanks a lot.

fposer at libero.it's picture
Joined: 2011-09-30
Reputation: 0

Here are two screenshots explaining the differences between the two
reports. Does this answer your question? If not I will explain in more
detail.

Steve Mignogna's picture
Offline
Joined: 2011-09-30
Reputation: 0

Don't you have the two reports switched? By the numbers that's what it
appears. You say the SS-D is sensible + latent and the LS-D is sensible
only, but the numbers and the report abbrev seem to say they're switched.

Karl Stum, PE

Karl Stum's picture
Offline
Joined: 2011-09-30
Reputation: 0

I do not think the two reports are switched. The main difference between
the two is that the SS-D report is the total coil loads that the system
sees, this includes outside air, duct losses, etc...

Steve Mignogna's picture
Offline
Joined: 2011-09-30
Reputation: 0