Curtain wall system - how to model baseline?

7 posts / 0 new
Last post

Hello,

I have a potential project in which the client is proposing a curtain wall
system.
The model will be based on ASHRAE 90.1-2013 Appendix G.
I believe the appropriate way to model this would be to have a WWR of 100%
(or near 100%) in the proposed case. For the baseline case, the window
area would have to be reduced to get the WWR down to 40%.
Is this the correct way or is there different guidance for modeling curtain
wall systems?

Thank you,
Mike Campbell

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Would there really be no opaque portions (aka spandrel) of the curtain wall? At the very least I?d expect you?d have about a 1? high slab-edge-bypass opaque section.

Our curtainwall projects (resi and office) typically have 40-50% vision glazing, and the rest is opaque, and gets modeled as a wall with calculated U-factor depending on the spandrel + inboard insulation configuration.

Nathan Miller, PE, LEED AP BD+C ? Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Thanks for the response Nathan.
There will be some spandrel glass, but I'm not sure how much.
But basically the spandrel portion would be considered a wall in the
baseline.
Only the transparent window assemblies would be considered in the WWR. Is
that correct?

Thank you,
Mike

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Spandrel (opaque) sections of curtainwall are ?walls? in both proposed and baseline cases as far as 90.1 terminology is concerned. Consider them as such for determining both Proposed and Baseline case WWR?s.

In my past year of experience, similar to Nathan, I?ve dealt with many ?fishbowl? buildings which appear all (or mostly) glass from the outside but typically have at least few feet of insulated envelope on the interior perimeter, so in that case it?s literally a wall construction with the outermost layer being glazing (or airspace then glass).

Be sure to dig up any relevant envelope sections/details to carefully draw the line between ?opaque? and ?not opaque.?

~Nick

Nick Caton, P.E.

Senior Energy Engineer
Energy and Sustainability Services
North America Operations
Schneider Electric

D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com
F 913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Makes sense - thanks for the input Nick and Nathan.

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Also if, you have conditioned spaces in an unconditioned parking garage (elevator lobbies, heated storage, mech/elec spaces, back of house space, etc), the walls that separate the conditioned space from unconditioned count in your wall areas, and typically don?t have much glazing, and help bring your proposed glazing % down.

Nathan Miller, PE, LEED AP BD+C ? Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

Great tip! Thank you