Dear All e-Quest Users
Please If someone can help :
1- for Sizing Ratio : 1.15 (for Cooling ? Equipment Efficiencies) , it should applied be for Baseline Model only ? or also it should be in Proposed Model ?
2- for Umnet Load Hours it should be under 300 Hours for Each Room/Zone ? or For the Total Building ? & where I can find the Umet Load Hours in e-Quest simulation Report
Thanks by Advance for all of u ??.
My Regards,
Riad el Abed
Chief MEP , LEED GA,PQP
Riad,
Q1- You can specify the selected fan capacity (cfm,static
pressure,...etc) in proposed model.
Q2- I do consider whole building unmethours should be <300 hrs. To see
the unmet hours,go to Air-Side HVAC / Summary. The last column "Hours
outside throttling range" represents the unmet hours.(attached screen
shot)
Hope this is helps.
Thanks
GK
Riad,
Q1- You can specify the selected fan capacity (cfm,static
pressure,...etc) in proposed model.
Q2- I do consider whole building unmethours should be <300 hrs. To see
the unmet hours,go to Air-Side HVAC / Summary. The last column "Hours
outside throttling range" represents the unmet hours.(attached screen
shot)
Hope this is helps.
Thanks
GK