Cooling Load not met!

3 posts / 0 new
Last post

Hi All,

I have created a System, which has only one zone(25000 sqft) using DX
coils for cooling, Furnace for heating; and system type is CAV Packaged
Single Zone system.

I have set the COOLING-CAPACITY = 1500.00 kBTU/hr.

When I was going through the HOURLY reports, I found the following data.

Below are the Peak Cooling Report Summary, followed by the HVAC Cooling
load for the peak day(Jun 21) and the current zone temperatures/
Thermostat Temperatures for that same day.

MY Queries are:

If my HVAC system is designed to remove a heat load of 1500kBTU, and the
total Heat to be removed on Jun21 (8am) was 1004375+44188 = 1048563 BTU/hr
only, why wasnt the HVAC system unable to remove it? The first doubt was
about insufficient CFM (of the used constant volume system). But the same
CFM is able to handle higher loads at other times.

Please see the SS-J Report during the particular hour the load was never
met.

Please resolve my confusion regarding this sufficient cooling capacity vs
unmet load scenarios.

I am attaching the inp, weather file for your reference (in case it
helps).

REPORTS:

REPORT- SS-J Peak Heating and Cooling for Sys1 (PSZ) (G.1) WEATHER
FILE- EPW New Delhi,Delhi,
---------------------------------------------------------------------------------------------------------------------------------

- - - - - C O O L I N G - - - - - - - - H E A T I N G - -
- D A Y C O O L I N G P E A K

JUN 14 JAN 19 JUN
21

HOURLY HOURLY HOURLY
COOLING SENSIBLE DRY- WET- HEATING DRY- WET-
COOLING SENSIBLE DRY- WET-
LOAD HEAT BULB BULB LOAD BULB BULB
LOAD HEAT BULB BULB
HOUR (KBTU) RATIO TEMP TEMP (KBTU) TEMP TEMP
(KBTU) RATIO TEMP TEMP

1 0.000 0.000 93.F 74.F 0.000 49.F 48.F
0.000 0.000 89.F 79.F
2 0.000 0.000 95.F 74.F 0.000 48.F 47.F
0.000 0.000 89.F 78.F
3 0.000 0.000 96.F 73.F 0.000 47.F 47.F
0.000 0.000 87.F 78.F
4 0.000 0.000 95.F 74.F 0.000 47.F 47.F
0.000 0.000 86.F 78.F
5 0.000 0.000 89.F 76.F 0.000 47.F 47.F
0.000 0.000 85.F 79.F
6 0.000 0.000 89.F 77.F 0.000 48.F 47.F
0.000 0.000 84.F 80.F
7 1100.896 0.763 89.F 77.F 0.000 48.F 48.F
1065.103 0.708 85.F 80.F
8 988.670 * 0.732 90.F 78.F 0.000 49.F 48.F
1004.375 * 0.685 86.F 80.F
9 996.547 0.747 92.F 78.F 0.000 51.F 50.F
988.282 0.686 90.F 81.F
10 982.636 * 0.731 94.F 79.F 0.000 52.F 51.F
1006.017 0.678 92.F 81.F
11 987.969 0.734 97.F 79.F 0.000 54.F 52.F
988.014 0.678 95.F 82.F
12 998.494 0.711 99.F 81.F 0.000 55.F 54.F
989.553 0.669 97.F 83.F
13 1004.154 0.694 100.F 82.F 0.000 57.F 54.F
990.271 0.662 98.F 84.F
14 979.070 0.691 100.F 83.F 0.000 59.F 55.F
955.878 0.668 99.F 83.F
15 934.561 0.711 100.F 81.F 0.000 59.F 55.F
942.959 0.676 101.F 83.F
16 863.300 0.735 100.F 78.F 0.000 59.F 55.F
899.941 0.683 101.F 82.F
17 737.102 0.770 99.F 75.F 0.000 58.F 55.F
814.377 0.687 102.F 82.F
18 0.000 0.000 97.F 75.F -6.497 56.F 53.F
0.000 0.000 101.F 81.F
19 0.000 0.000 96.F 74.F 0.000 53.F 52.F
0.000 0.000 100.F 81.F
20 0.000 0.000 94.F 76.F 0.000 51.F 50.F
0.000 0.000 98.F 81.F
21 0.000 0.000 93.F 77.F 0.000 49.F 49.F
0.000 0.000 98.F 82.F
22 0.000 0.000 91.F 78.F 0.000 48.F 48.F
0.000 0.000 96.F 81.F
23 0.000 0.000 90.F 78.F 0.000 48.F 48.F
0.000 0.000 95.F 81.F
24 0.000 0.000 89.F 78.F 0.000 49.F 48.F
0.000 0.000 93.F 81.F
-------- -------- ---------
SUM 10644.770
MAX 1100.896 -6.497

SYSTEM-TYPE PSZ SQFT/TON 544.9
COOLING PEAK 22.02 (BTU/HR- SQFT) HEATING PEAK
-0.13 (BTU/HR- SQFT)
SUPPLY AIR PEAK FLOW 0.53 (CFM/SQFT) MIN-OA/PERSON
35.00 (CFM )
OA FRAC AT CLG PEAK 0.164 OA FRAC AT HTG
PEAK 0.164

* ASTERISKS INDICATE HOURS LOADS NOT MET
---------------------------------------------------------------------------------------------------------------------------------------------------

BUILDING Zn (G.1)
-HVAC
COOLING LOAD NOT
LOAD MET
BTU/HR BTU/HR

----( 1) ----(16)
621 7 1065103. 0.
621 8 1004375. 44188.
621 9 988282. 0.
62110 1006017. 0.
62111 988014. 0.
62112 989553. 0.
62113 990271. 0.
62114 955878. 0.
62115 942959. 0.
62116 899941. 0.
62117 814377. 0.

DAILY SUMMARY (JUN 21)

-------------------------------------------------------------------------------------------------------------------------------------------------
Zn (G.1) Zn (G.1)

ZONE THERMOST
TEMP SETPOINT
F F

----( 6) ----( 7)
621 7 76.9 76.0
621 8 79.4 76.0
621 9 76.9 76.0
62110 77.0 76.0
62111 76.9 76.0
62112 76.9 76.0
62113 76.9 76.0
62114 76.8 76.0
62115 76.8 76.0
62116 76.7 76.0
62117 76.6 76.0

DAILY SUMMARY (JUN 21)

Regards,
Siddharth Venkataraman

Siddharth V's picture
Offline
Joined: 2011-09-30
Reputation: 0

Siddharth:

It would help if you attach the .pd2 file also.

Paul Diglio

Paul Diglio's picture
Offline
Joined: 2011-09-30
Reputation: 400

Hi Siddharth

When I had issues with unmet load hours recently, it turned out to be the
temperature control setpoints. I produced an hourly report with air
temperatures at various parts of the air handling system, and was able to
see that the control for the supply temperature was causing the problem.

I hope this helps.

MaryAnne