Dear all,

ASHRAE 90.1 - 2007, App G
typical office building
Climate zone 4a

A mixing box should operate predominantly on re-circ whilst introducing a
minimal amount of fresh air to the building (such as that required to meet
ASHRAE 62.1).

Does anybody else find the tables G3.1.2.6A & B confusing?

Cheers

Chris

Chris Yates2's picture
Offline
Joined: 2011-10-02
Reputation: 0

Sorry this was a question! I was just trying to be concise but realised
when I re-read that it was incomplete.

It appears that an economizer is not applicable to a baseline building in
this case. However, G.3.1.2.6B infers that there may still be a high limit
shutoff.

I thought the high limit shutoff was the economizer!

Grateful for your longsuffering patience!

Chris Yates2's picture
Offline
Joined: 2011-10-02
Reputation: 0

Dear Chris,
4a does not appear to be referenced in Table 6B...
Regardless, the two tables go together and a high limit is not applicable if no economizer is used.
p.s., I don't recall, but I think my red marks reflect some addenda.

[cid:image001.png at 01CF1CBF.CCF519E0]

James V Dirkes II, PE, BEMP, LEED AP

James V Dirkes II, PE's picture
Joined: 2011-10-02
Reputation: 203

I'm with Jim.

G3.1.2.6.B and corresponding section G3.1.2.7 do not kick in if economizers aren't required.

~Nick

Nick-Caton's picture
Offline
Joined: 2011-09-30
Reputation: 805

Brilliant. Thanks everyone.