Building Peak Cooling Load

2 posts / 0 new
Last post

Hello,
Which report shows actual building peak cooling load? Is it the SS-D
report? I am modeling ASHRAE 90.1 2007 system 8 - VAV w/PFP boxes and have
chillers in baseline case. Shall I look at the SS-D report peak cooling
load or PS-C equipment peak cooling load? I am getting different values in
both reports(SS-D = 529.22 tons and PS-C = 642 tons).

*Siddharth*
?

via Equest-users's picture
Joined: 2016-07-15
Reputation: 400

As a general practice I?d advise referencing the net peak listed for the baseline CHW loop in the PS-D report for determining plant peak cooling load, independent of chiller distribution.

One difference between the numbers is that where SS-D is simply the peak load seen at the HVAC coils, the PS-D figure incorporates heat of CHW pumping & distribution, which is additionally handled at the primary equipment. I?m not sure if that explains the whole gap you?re seeing, but that?d be a part of it.

~Nick
[cid:image001.png at 01D321B5.8BBE0640]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric