Dear E-questers,

I am working on a hospital building project which uses existing heat pump
at site for service water heating.

The issue is arising in modeling baseline hot water system, which as per
ASHRAE 90.1-2013 Table G3.1.1-2 is specified as gas storage water heater
for hospital building type. The gas utility rates will not be available for
the project since no gas heating system is used at site.

I want to confirm whether identical system as proposed case can be
considered in baseline model as the energy cost savings will need to be
compared with existing heat pump at site.

Thanks in advance.

Rushi Quest's picture
Offline
Joined: 2019-12-11
Reputation: 0

Hi Rushi,

The exception to Table G3.1.11.j (Baseline) states that you should use propane at the fuel source in the baseline when natural gas is not available at your site. In that case, it?s up to you to find a price for propane in your area or use EIA?s propane prices website like https://www.eia.gov/dnav/pet/pet_pri_wfr_dcus_nus_w.htm.

Alex Chapin EIT, BEMP, LEED AP BD+C, O+M
Energy Engineer | Mason & Hanger
A Day & Zimmermann Company
O 804.521.7072
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
masonandhanger.com

An ISO 9001 Certified Company

Building a More Secure World ?

CAUTION - THIS EMAIL MAY CONTAIN CONFIDENTIAL INFORMATION

This electronic mail transmission and any accompanying documents may contain information belonging to the sender, which may be proprietary, confidential, and/or otherwise subject to restrictions on disclosure beyond the intended recipient. This information is intended only for the use of the individual or entity to whom this electronic mail transmission was sent as indicated above. If you are not the intended recipient, any disclosure, copying, distribution, or action taken in reliance on the contents of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please call 1-703-955-5702 and delete this transmission. Thank you.

ChapinAN's picture
Offline
Joined: 2019-01-19
Reputation: 0

I agree with the guidance/discussion so far (the Standard is relatively clear in prescribing natural gas, or possibly propane if your AHJ/rating-authority accepts), but I?m left a little unsatiated? Can we take a step back and discuss the Standard a little further?

What could be the basis or rationale for 90.1 deciding to diverge from ?baseline should match the existing system, as applicable?? Prescribing a service water heating system on the basis of building occupancy certainly adds extra nuance/complexity, and demonstrably can result in existing/real service hot water baseline systems being represented with potentially unrealistic system/fuel types.

I trust the 90.1 committee made this change with deliberation, and fully expect I am missing some part of the bigger picture, but would like to be educated if anyone has a sense of why we?re moving in this particular direction.

Thanks!

~Nick

For mutual reference, In 90.1-2010 Table G3.1 reads as follows:
[cid:image002.png at 01D6869E.F908B320]
With 90.1-2013, the same passage (highlighted) was revised as follows:
[cid:image005.png at 01D6869E.48012E40]
[cid:image007.png at 01D6869E.48012E40]
And here is the referenced table:
[cid:image008.png at 01D686A1.9B174B20]

[cid:image006.jpg at 01D68773.5A941010]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Energy and Sustainability Services
Energy Performance Contracting
D
M
E

913 . 564 . 6361
785 . 410 . 3317
nicholas.caton at se.com
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219

[cid:image003.png at 01D6869B.3CE5BBF0]

Nicholas Caton2's picture
Offline
Joined: 2019-03-25
Reputation: 0