ASHRAE 90.1 fan power limitation calculation question

3 posts / 0 new
Last post

For the baseline fan power limitation, the pressure drop allowances are defined. I am a bit fuzzy on the definition of "Return/Exhaust Control Devices". A system with a return fan and OA economizer typically has dampers to control the flow of the OA, return/exhaust air streams. Would these dampers qualify as a Return/Exhaust Control Device?

[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065

www.wspgroup.com

________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP?s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership

Jones, Christopher's picture
Joined: 2015-06-11
Reputation: 0

Here is an abstract from 90.1 User?s Manual that answers your question:

Pressure Drop Adjustment Devices

This section provides a description of the

types of devices that quality for additional

fan power. ?

???

Return and/or exhaust airflow control devices.

Some types of spaces such as laboratories,

test rooms, or operating rooms require

that an airflow control device be provided

at both the supply air delivery point and at

the exhaust. The exhaust airflow control

device is typically modulated to maintain a

negative or positive space pressure relative

to surrounding spaces. An additional

pressure drop and associated brake

horsepower adjustment is permitted when

this type of device is installed. The credit

may be taken when some spaces served by

an air handler have exhaust airflow devices

and other spaces do not. However, the

credit is taken only for the CFM of air that

is delivered to spaces with a qualifying

exhaust air flow device.

--

Maria Karpman LEED AP, BEMP, CEM

________________

Karpman Consulting

www.karpmanconsulting.net

Phone 860.430.1909

41C New London Turnpike

Glastonbury, CT 06033

Maria Karpman's picture
Offline
Joined: 2011-09-30
Reputation: 0

HI Chris,

The base fan power allowance already includes the necessary pressure drop for return/exhaust dampers in the air handler. The adjustment for exhaust/return control devices refers to damper boxes or other devices used to control space pressurization like you would typically find in a laboratory or hospital.

Cheers,

Michael Tillou, PE, LEED AP BD+C, ASHRAE BEMP

Associate

Atelier Ten

Environmental Design Consultants + Lighting Designers

45 East 20th Street, 4th Floor

New York NY 10003

T +1 (212) 254 4500 x208

F +1 (212) 254 1259

michael.tillou at atelierten.com

www.atelierten.com

Michael Tillou's picture
Offline
Joined: 2011-10-02
Reputation: 0