I'm modeling a lab where general lab exhaust is run through an energy
recovery unit, while fumehood exhaust is exhausted directly.

I don't see a spot in eQUEST where you can specify the airflow through
an energy recovery unit. Is it possible?

Vikram Sami, LEED AP

Vikram Sami's picture
Offline
Joined: 2011-09-30
Reputation: 0

Vikram,

You can enter it in the Heat Recovery 1 Tab:

I think if you specify the zone OA cfm and the zone exhaust (if any),
the ERV cfm will take care of itself even if you don't enter it
explicitly.

Regards,

William Bishop, EIT, BEMP, LEED(r) AP