I'm modeling a lab where general lab exhaust is run through an energy
recovery unit, while fumehood exhaust is exhausted directly.
I don't see a spot in eQUEST where you can specify the airflow through
an energy recovery unit. Is it possible?
Vikram Sami, LEED AP
Vikram,
You can enter it in the Heat Recovery 1 Tab:
I think if you specify the zone OA cfm and the zone exhaust (if any),
the ERV cfm will take care of itself even if you don't enter it
explicitly.